As usual the handbook does a better job of explaining things. This is commentary from 250.122
"Equipment grounding conductors on the load side of the service disconnecting means and overcurrent devices are sized based on the size of the feeder or branch circuit overcurrent devices ahead of them."


Greg Fretwell