What article in the code would not allow a 3 Conductor SER cable to feed a sub-panel? An inspector is telling me the cable has to have an insulated neutral.
I ran the cable from a 200A MAIN CSED outside to a 200A load center in a basement. I ran ground wires along with the cable.
If there is an article that would allow this please let me know.
Please look at 250.142 B EX:2
Thanks for any replies.
-regards
greg