Look at Table 514.3(B)(1). If the receptacle and card reader are outside of the classified areas they can be installed. If the conduits to the recepacle and card reader pass through the classifed area, then bondary seals will be required. This would require that both conduits have seals at the island as well as at the building.
Don


Don(resqcapt19)