txsparky,

Are you saying that Entergy requires that neutral be bonded to the meter socket ground even if the neutral is bonded to the ground elsewhere?

I would read the paragraph that you quote as requiring that the meter socket be grounded, but _not_ requiring that the neutral be bonded to ground in the meter socket. If the bond between neutral and ground is elsewhere (eg in the main disconnect), then the customer is responsible for proper ground continuity to between the meter socket and the point of the ground bond.

I don't see a required parallel path unless it is required to bond ground to neutral in the meter socket.

-Jon