I would take 'objectionable'to mean that someone would complain, but they are not...
so here's the deal.........
240v open delta 3 ph pole mount x-formers feed pole mounted meter, load side had 2 runs (there is no main) to ...
a) poolhouse w/ 3ph panel & 3 ph 7.5 hp pump motor
b) lifegaurd shack/toilet/concession stand 20 cir 1 ph panel
now each building has a municipal H2O line, both metal, both used as a GEC.
there is also a chain link fence that circles the pool and travels from poolhouse to baywatch central
each is serving as a rather efficent noodle
any objections?