Cindy,
Look at 408.21. The listing has not permitted two or more grounded conductors under the same screw for a long time. The UL listing requirement was the reason that 408.21 was added to the NEC. The listing does permit more than one grounding conductor under a screw.
Don


Don(resqcapt19)