The exception is not very likely to apply here since, generally speaking, paralled conductors must be 1/0 AWG or larger.

Unless you're dealing with some of the exceptions to the paralled conductor rule (unlikey) I don't know why this would come up.

All the fine print on those little labels inside the cabinet need to be read to see if any of the terminals are in fact listed for two conductors.