A quick and dirty answer is:

The "Neutral" [Better known as the Grounded Circuit Conductor] is no different than any other circuit conductor - only it is usually Grounded.

On a simple 1 phase 3 wire system, the "Neutral" is derived from a "Center Tap" on the secondary winding.
This center tap effectively cuts the winding's normal output voltage of 240 VAC by half, so from each "End" of the secondary winding to the Center Tap, the Voltage is 120 VAC.

It does not need to be Grounded for this to function properly - nor any other "Common Grounded Circuit Conductor".