Thanks Fred. I was looking at the HOMELINE section not the QO. They must be using a 200 amp buss in this panel.

Here in CA we don't use main breaker load centers much and most of the supply houses don't stock many of them. We always install a combination service entrance device and use main lug load center for sub panels. If we do need a main breaker we use a convertible load center or back feed a breaker with a retainer.

Curt