Sparky,
The code only says it can't be in the shower space. It is permitted to be within reach.
Quote
404.4 Wet Locations.
A switch or circuit breaker in a wet location or outside of a building shall be enclosed in a weatherproof enclosure or cabinet that shall comply with 312.2(A). Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.
Don(resqcapt19)


Don(resqcapt19)