2002 NEC:
300.21 Spread of Fire or Products of Combustion.
Electrical installations in hollow spaces, vertical shafts, and ventilation or air-handling ducts shall be made so that the possible spread of fire or products of combustion will not be substantially increased.
Openings around electrical penetrations through fire-resistant-rated walls, partitions, floors, or ceilings shall be firestopped using approved methods to maintain the fire resistance rating.
FPN: Directories of electrical construction materials published by qualified testing laboratories contain many listing installation restrictions necessary to maintain the fire-resistive rating of assemblies where penetrations or openings are made.
Building codes also contain restrictions on membrane penetrations on opposite sides of a fire-resistance–rated wall assembly.
An example is the 600-mm (24-in.) minimum horizontal separation that usually applies between boxes installed on opposite sides of the wall.
Assistance in complying with 300.21 can be found in building codes, fire resistance directories, and product listings.
Go to http://www.ul.com for more information.