I would agree with Tom, however, with one added note. Since, per 220.3(B)(10), the load calculations of general-use receptacle outlets for dwelling units are included in the general lighting load calculations from table 220.3(A), which is based on 3VA per sq. ft. The load (number of receptacles) shall be evenly proportioned among the multioutlet branch circuits within the panelboard, per 210.11(B). So if you had a branch circuit that was not evenly proportioned as compared to the other receptacle outlet branch circuits in the panelboard, the inspector would be correct in not passing the installation.