Pete brought up bonding in another thread. 250-148(a) requires the EGC to be connected to the box, however, in Nebraska the AHJ does not have a unanimous opinion that this is a good thing, so most inspectors are not enforcing it. We always run a EGC, even where we would be allowed to use the raceway as the ground.

The company opinion is that bonding at the box creates parallel paths for the ground and that's a bad thing. Bottom line is we don't do it because it takes more time and the AHJ doesn't enforce it.

What do you think?

GJ