See Section 384-10 in the 1996 or 1999 NEC and 408.10 in the 2002 NEC.

"The conduit or raceways, including their end fittings, shall not rise more than 75 mm (3 in.) above the bottom of the enclosure."

Measure to see if this rule is violated?


Joe Tedesco, NEC Consultant