Most people would cobble this together, making it bad. But as mentioned, I think it could be done well:
  • Receptacle behind drawer
  • 12/3 SO with NEMA 5-15 plug and strain relief, going to strain relief at drawer
  • Permanant, boxed receptacle inside drawer
  • Cabinet bellow drawer to allow access
  • Drawer short enough not to crush cord
That way it's not hard-wired, it's accessable, it has a disconnect means, it's not subject to damage, it doesn't need additional OCP. Unless I'm missing something, I don't see the problem if carefully executed.

All that being said, it would be much easier, and much less questionable to simply put a receptacle in a cabinet and put the chargers in there.

-John

[This message has been edited by BigJohn (edited 12-22-2006).]