if the panel is labeled as 3phase 208/120v,wouldn't you be required to feed it as such,
I don't think so.
Any more than you have to feed a 225 amp panel with 225 amps.
Or any more than you have to supply a Square D I line at 600 volts just because it is able to handle that voltage.
IMO where you would run into trouble is when you try to supply a straight three phase panel with Wye.
But then again, I don't share neutrals either.
Actually you share neutrals with every circuit on the supply side of the source.
Electrons do not know or care which side of a panel they are, they act the same either way.
You can deny it to be true if you want but I challenge you to show how it differers electrically from one side of a panel to the another.
BTW I had to bring two branch circuits to each of two 9 panel LED screens at a concert venue.
You'll never guess what the vendor specified.
An L21-30R
Thats 3 hots with one neutral for those following along at home.
It worked flawlessly and aided in combating voltage drop on the 400' runs of 6 AWG.