BTW - Appendix C, pg. 585 does say 4 #1 are allowed in 1-1/4" EMT; however if you do the arithmetic from Table 4 & Table 5 (EMT usable space & area of THHN tables)you cannot use 4 #1s in 1-1/4" EMT.

However, even though you are allowed to use the EMT as the EGC, I highly recommend you do pull the #6 (the arithmetic works) as your EGC - don't trust the EMT connection over the years to be maintained and work when needed in the event of a fault.