Looking at a R.V. park voltage drops on distances so great. Ideas???. 35 sites two 50 ampers then rest 30-20 amp aprox 100ft to ist then 80 ft between each & two rows.
Makes for some long runs
9600x2=19200 plus 3600 x 33=138000
138000 x 42%(table 551.73)=57960 divided by 240=241.5 amps.
for service calculations .
each row I take it also by 551.73

Pnl ---------------------------------------
----------------------------------------
around 1400 ft each row
additional rows i know would help.
lugs at most good fer 250mcm '
more rows possibly needed
anyone run into this before?