I would suggest considering a multi-wire-branch-circuit for this load. If you put 5 posts on each leg, alternating, then you could use #8 conductors and meet your voltage drop requirements.

Remember to increase the size of the equipment grounding conductor at the same time that you upsize the supply conductors.

If you place the receptacle on this circuit, then you are limited to using 20A breakers.

-Jon