Everything must be 3p rated and for the applied voltage.
Some standard single phase equipment is listed for use on corner grounded delta systems. There is no need for overcurrent protection in the grounded phase. Also, many forget that the rules in Article 200 apply to the grounded conductor in this system.
Don


Don(resqcapt19)