OK there are many ways to do it, the most accurate would be point to point.

That means figuring the VD separately for each segment.

However your total load is low 5 x 150 watts or 6.25 amps so you might do fine by figuring 6.25 amps at 250' out.


Bob Badger
Construction & Maintenance Electrician
Massachusetts