Ungrounded systems are common in powerplants or substations. That way, IF one phase does become grounded, life goes on. Control of operations isn't effected.
Now a ground on a 2nd phase is another thing.

But I agree with Winnie. You most likely have a corner grounded system.If that is the case, your phase to ground reading is irrelevant.

HP