Normally open non-addressable fire alarm devices such as smokes, pulls, heats etc. must be wired parallel.

Normally closed trouble indicators like tamper switches, pressure switches other panel trouble contacts etc. can be wired in series.


Bob Badger
Construction & Maintenance Electrician
Massachusetts