Calculate the loads using 220.82.
Where are you getting the 30 amps for the A/C? You need to use the actual load of the unit not the maximum fuse/breaker size. I can’t imagine this space needing more that 2.5 - 3 tons which would be around 20 amps.


Curt Swartz