The only reference to wet bar sinks is 210.8(A)(7).

I do not know of a reference in the NEC that even requires the wet bar counter to have receptacles, let alone having 2 circuits.


Branch circuits required - 210.11(C)

Receptacles required - 210.52

no mention of wet bars in these sections.