Dave,

Unless you have a 208/120, 3 phase service you can't use the 208v tap. The 217v to ground that you are measuring is the normal voltage for the "wild" leg on a 240v, 3ph. service.

Do not use the wild leg except for 240v loads. It is not a 208v leg.