Electric Ian

Quote
Do you typically install a GFCI for a garbage disposal receptacle?

Are you asking if it is required?

Depends, commercial kitchen or dwelling unit kitchen?

In a dwelling unit kitchen only 15 and 20 amp receptacles that serve counter tops must be GFCI protected.

So a disposal outlet under the counter is not required to be GFCI protected.

In a commercial kitchen if you did have a cord connected disposal connected to any 15 or 20 amp 120 volt receptacles it would be required to be GFCI protected.

ALL 15 & 20 amp 120 volt receptacles in commercial kitchens must have GFCI protections...no exceptions.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts