Quote
Another thing I see a lot of is POINT OF ATTACHMENT BELOW WEATHER HEAD!

It is required to be below the weather head.

Quote
230.54(C) Service Heads Above Service-Drop Attachment. Service heads and goosenecks in service-entrance cables shall be located above the point of attachment of the service-drop conductors to the building or other structure.

Exception: Where it is impracticable to locate the service head above the point of attachment, the service head location shall be permitted not farther than 600 mm (24 in.) from the point of attachment.

This just came up at another forum and I messed it up big time. shocked

But in the end IMO, we decided the point of attachment is required to be below the weather head.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts