No you can't use 16-2........once you hit the transformer and switch to DC the farther away you get the more problems you have.

I would say you shouldn't use 16/2 but you can with the proper OCP. The NEC does not care if there is voltage drop only that the conductor is protected at or below the conductors rating.

Voltage drop is strictly a design issue.

As a side note most, if not all low voltage lighting systems run AC power.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts