This may seem like a dumb question but if you connect different size transformers in parallel to divide the load what keeps the smaller transformers from being overloaded?
Lets say you have a 1000 amps of load and 4 transformers feeding it, three transformers rated 300 amps one transformer rated 100 amps.
In the above example I would expect the 100 amp transformer to release smoke as it will be loaded to approximately 250 amps.
How does this work?
Confused, Bob