I just replaced two trip units from Westinghouse (CH) molded case breakers because of the loud wining and sizzle noise on elevator inrush.

Voltage drop was less than 100mV, and nothing on the IR. I used my ultraprobe to pinpoint which breakers were the culprits.

Noise is gone.