You can not share a neutral on the LOAD side of these devices. A fault is sensed thru the neutral, a split return path. If you are using a shared neutral on these circuits you can pigtail each neutral to the device and you should be fine. You can share on the line side. These devices are "blind" on the line side. All would be legal but only one will work!


Kenny Wilee