I'm running a u/g feeder via pvc from a combination meter/main panel on a customer owned pole approx. 160 ft. to a dwelling and will enter through the foundation wall.
200A service so it will be 3 2/0 cu conductors and a #6 EGC. The run has one 90 degree bend.
My question concerns sizing the pvc conduit.
I thought I'd use a sched.80 sweep 90 and sched 40 the remainder of the run. I was told that sched. 80 holds up to pull rope better. Tables 9 & 10 tell me that 2" pvc can contain up to 5 2/0 THWN for sched 80 and 6 2/0 THWN for Sched 40. Should I consider running larger PVC? I managed to borrow a tugger but this aspect of the job worries me the most.
Don