The trip curve that I looked at from another manufacturer shows that the trip time for a load equal to 125% of the breaker rating will be between 1000 seconds and never. The GE trip curve in the link does not show the maximum trip time for a 125% load. The time in that table stops at 1000 seconds.
Don


Don(resqcapt19)