C-H,
There is no "trick" required to make the GFCI work. If there is more than ~5 mA of leakage current the GFCI will open the circuit. If there is less than than, the GFCI will not trip, but that level of shock is not a serious hazard to most people.
250.34(C) requires that the neutral be bonded to the generator frame. 250.34(A) requires that the ground terminal of the receptacle be bonded to the generator frame.