I will always try to include a 3 to 4 wire upgrade in such a service change, however if we would like to delve into the NEC:

250-140's key word is 'existing'

250-142(b) EX #1 states;
The frames of ranges, wall mounted oven, counter-mounted cooking units, and clothes dryers under the conditions permitted for existing installations by Section 250-140 shall be permitted to be grounded by a grounded conductor

Ok, so tape that puppy up & off to the N-bar!

BUT WAIT !

90-5(b) Permissive Rules
nice if you do it, but don't gotta!

Ok, so on to the G-bar???

BUT WAIT!

Art 100, Special Permission;
basically what Tom said

So can we do a poll of AHJ's here?
Door #1--Noodle Bar
Door #2--G-bar
Door #3--rejected until a 4-wire set-up


[Linked Image]