LarryC:

IMHO, the inspection process on MCCs (Control Cabinets) "stops" at the feeder.

"Equipment" that is remote from the MCC requires NEC conformance as to the wiring methods and OCP.

The 'interior' of the MCC is the responsibility of the mfg. and MUST have listing/label from a NRTL.

I assume your equipment has a NRTL listing/label, so if they are OK with the crimp terminations and FS conductors, that would be OK with me.



John