This service is for a "permanent" construction camp. It has been running on Generators for a year and we are doing the permanent hookup. The reason the disconnect was non fused was because the Gen has a main breaker so the original contractor thought they'd save a few bucks. Inspector Says disconnect must be fused as the consumer service starts at the meter(transformer). I would have included a picture but don't appear to have the mental faculties for that.
(PS digging in frozen ground does suck....but hydrovac trucks make it easier.. although messier).