Hello, I'd like some input from licensed electricians in MA please.
I'm a home inspector and I have a builder who wants to install 2 4-wire 30amp outlets on a single 30amp double-pole breaker in a detached garage workshop (arc weld,etc.). Not being a licensed electrician, I can't site the actual code on this one, but my gut is that it's better off being 2 separate circuits. The owner claims that due to his needs he would never be running both at same time. I say, what about the next guy who buys the house who has different plans?
Are these outlets even really engineered to be daisy chained?
Also, even if they were pig-tailed in a separate j-box, the argument that they're protected against overload by the breaker tripping seems weak. I see a tripping breaker as a last line of defense against fire, not something I really want to rely on if I can help it. I've seen so many corroded breakers that don't trip when needed.
What do you guys think? Is there an actual code that says you can or cannot do? Or is this up to the local electrical inspector.
Thx- Joe