Originally Posted by HotLine1
You have to determine the OCP that you are installing to determine the EGC for the circuit.

Using the nameplate MAX of 25 OCP would require #12. This is based on 250.122 table in '11 NEC as I read it.



I use the Minimum Circuit Ampacity to size my branch circuit conductors for an AC unit...