BigB, the question is not whether it is possible to place a receptacle - the point is that such design elements remove the requirement for receptacles .... or prohibit you from 'counting' the receptacles you do instal.

For example, an 'appliance garage' might very well have a receptacle in it. You are not,however, allowed to consider it as one of the 'counter' receptacles. Yet, the positioning of the garage might very well eliminate wall space - removing the requirement for there to be any receptacle.

Greg has a point about wall spacing. My previous home had a kitchen 'counter' area that was broken up into numerous sections that were too small for the receptacle requirement to kick in. Imagine - eight feet of 'counter,' and no receptacles required. Now THERE would be a real challenge to provide the two required SABC's, without exceeding 'minimum' code.