Just don't forget what John said about bonding the water pipe in each unit. This is a bond, not a ground electrode. I know the electrons don't know the difference but you can use smaller wire per 250.104(A)(2). That will be #8 for a 150a feeder supplied unit instead of the 1/0 you probably end up with on the service side from 250.66.