within a raceway


Really?

How is that accessible? It is OK in a condolet tho.

Quote
300.13 Mechanical and Electrical Continuity — Conductors.
(A) General. Conductors in raceways shall be continuous between outlets, boxes, devices, and so forth. There shall be no splice or tap within a raceway unless permitted by 300.15; 368.56(A); 376.56; 378.56; 384.56; 386.56; 388.56; or 390.6.


Each of those "unlesses" refers to a removable cover.


Greg Fretwell