I could use some opinions on this inspection. Contractor is asked to provide power for an igniter for a "Fire Bowl" located on the coping of an in ground pool. The igniter is 24v. and my feeling is that even tho he bonds the metal parts, and provides GFCI protection for the xformer feeding the igniter he is not permitted to do this because of 680.22 (E). I think the "Fire Bowl" igniter will be within the 10' range. Hope this link work. www.grandeffectsinc.com if it doesn't, copy it into your browser and take a look at this produce. It is Listed (I think) but I haven't gotten any response to my email.