Reno:

OK, I apologise for using 'semi rant'. You are 100% right on about a good counter guy (or gal, to be PC). A good feeling is the counter guy saying 'ya need glue?' when you hustle in & pick up 500' of 4" PVC!!

Above you say:
"Just to again illustrate the point .... we have that 'new' code requirement for panels to have some manner of 'intersystem grounding termination.'"

Are you refering to 250.94? from 2008 changes, aka: intersystem bonding termination? We've been enforcing that since Oct. 2009, and still have the occasional guy fail for not installing it. Most ECs here use the Arlington item, about $12 as our utilities do not allow any of the 'items' that mount to the meter pans.

I'm curious, what did you find for $50??

Now, if you want to talk real scary....how about the 'experts' in some of the big box stores!!


John