Adrian...

Nope.

Only voltage superiority injects power.

The frequency can't be tampered with -- such would create crazy harmonics.

The inverter sends power to the system by staying entirely in synch...

But at a trivially higher voltage. That's all it takes.

Because of voltage drop over distance -- the local loads will 'feel' the PV first.

Only after they are saturated by the PV array will enough 'over-voltage' remain for energy ( joules ; watt-seconds ) ever make it out into the grid.

Leading the Poco's frequency absolutely DOES NOT WORK. Instead, you would impose a harmonic upon the grid...

Something that would draw finger wags from the Poco.


Tesla