When I opened a neutral splice in a fluorescent fixture once, that was still energized it felt like I was kicked in the head by a horse! shocked dunno

410.130(G) Disconnecting Means.

(1) General. In indoor locations other than dwellings and associated accessory structures, fluorescent luminaires that utilize double-ended lamps and contain ballast(s) that can be serviced in place shall have a disconnecting means either internal or external to each luminaire. For existing installed luminaires without disconnecting means, at the time a ballast is replaced, a disconnecting means shall be installed. The line side terminals of the disconnecting means shall be guarded.

Exceptions are open for discussion. Also what is different about "dwellings and associated accessory structures"?


Joe Tedesco, NEC Consultant