By table 310.15, #3 Cu SE is good for 110 amps, so a 100 amp cb would be compliant.
Is this type of SE cable is rated at 60°C rating or on 75°C rating I know this is for service entrance but if used for feeder then the bet is off it have to stay with 60°C rating.
Merci,
Marc