Originally Posted by wewire2
... I see disconnects on AC condensers that would block the access for replacing the compressor motor. The inspectors never seem to mind. What do you think??

The last part of 440.14 is intended to prevent that.
Quote
440.14 ...The disconnecting means shall not be located on panels that are designed to allow access to the air-conditioning or refrigeration equipment or to obscure the equipment nameplate(s).


Don(resqcapt19)