It gets back to "are they likely to be energized" and that is an AHJ call. What size wire does he want you to use and will he just let you use the EGC of the circuit that is likely to energize the pipe? (usually the appliance on the end of the pipe).
That was my take on 250.104(B)

Quote
(B) Other Metal Piping. Where installed in or attached to a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.


Greg Fretwell